Sections
250.2 Definitions Continued
Ground (Earth) [100]. Earth or a conductive body that is connected to earth. Figure 2506
Grounded [100]. Connected to earth.
Ground Fault [100]. An unintentional connection between an ungrounded conductor and metal parts of enclosures, raceways, or equipment. Figure 2507
Ground-Fault Current Path [250.2]. An electrically conductive path from a ground fault to the electrical supply source.
Authors Comment: The fault-current path of a ground fault is not to the earth! Its to the electrical supply source, typically the X0 terminal of a transformer.
FPN: The ground-fault current path could be metal raceways, cable sheaths, electrical equipment, or other electrically conductive materials, such as metallic water or gas piping, steel-framing members, metal ducting, reinforcing steel, or the shields of communications cables. Figure 2508
Authors Comment: The difference between an effective ground-fault current path and fault-current path is that the effective ground-fault current path is intentionally constructed to provide the low-impedance fault-current path to the electrical supply source for the purpose of clearing the ground fault. A ground-fault current path is simply all of the available
conductive paths over which fault current flows on its return to the electrical supply source during a ground fault.
Grounded (Earthed) [100]. Connected to earth.
Grounded Neutral Conductor [100]. The conductor that terminates to the terminal that is intentionally grounded to the earth. Figure 2509
Grounding (Earthing) Conductor [100]. The conductor that connects equipment to the earth via a grounding electrode.
Authors Comment: An example would be the conductor used to connect equipment to a supplementary grounding electrode [250.56]. Figure 25010
Figure 250–6
Click on Image to Enlarge
Figure 250–7
Figure 250–8
Figure 250–9
Figure 250–10