2005 NEC Changes Summary
Articles 725 through 770
ARTICLE 725 Class 1, Class 2, and
Class 3 Remote-Control, Signaling, and Power-Limited Circuits
Circuits that fall under Article 725
are remote-control, signaling, and power-limited circuits that aren't an integral part
of a device or appliance. Article 725 includes circuits for burglar alarms, access control,
sound, nurse call, intercoms, some computer networks, some lighting dimmer controls and
some low-voltage industrial controls.
Let's take a quick look at the types
of circuits:
- A remote control circuit controls
other circuits through a relay or solid-state device, such as a motion-activated security
lighting circuit.
- A signaling circuit that provides
an output that is a signal or indicator, such as a buzzer, flashing light or annunciator.
- A power-limited circuit operates
at no more than 30V and 1,000VA
We'll cover these definitions in more
depth later and explain the differences between Class 1, Class 2 and Class 3.
The purpose of Article 725 is to allow
for the fact that these circuits "are characterized by usage and power limitations
that differentiate them from electric light and power circuits." Article 725 provides
alternative requirements for minimum wire sizes, derating factors, overcurrent protection,
insulation requirements, wiring methods and materials.
As with all other articles in Chapters
5 through 8, the wiring methods required by Chapters 1 through 4 apply [90.3]. But because
of the inherently lower danger of fire risk with qualifying circuits, Article 725 specifies
conditions where these methods aren't required. For example, you do not need to put a
Class 2 splice in a box or enclosure. At the same time, additional requirements apply
to ensure safety. While there's not a net compromise on safety, there's a net cost-savings.
Article 725 consists of three parts.
Part I provides general information, Part II pertains to Class 1 cabling, and Part III
pertains to Class 2 and 3 cabling. The key to understanding and applying each of the three
parts is knowing the voltage levels of the cabling involved and the purposes of that cabling.
Article 725 allows you to save time and money when working with particular types of circuits.
- Text revised to specify that
accessible portions of abandoned Class 2, Class 3, and PLTC cables must be removed.
- Changes clarify the types of
cables and raceways permitted in ducts, plenums, and other space used for environmental
air.
- This section was revised to
clarify that it's the equipment supplying the circuit that must be durably marked
to indicate each Class 2 or Class 3 circuit.
- New rule prohibits the installation
of audio system circuits in the same cable or raceway with Class 2 or Class 3 conductors
or cables.
- New sentence identifies the
type of nonmetallic raceway containing Class 2 or Class 3 cables that is permitted
in "other spaces used for environmental air."
- New subsections added to recognize
the use of raceways designed for Class 2 and Class 3 cables.
ARTICLE 760 Fire Alarm Systems
Article 760 provides the requirements
for the installation of wiring and equipment for fire alarm systems, including all circuits
the fire alarm system controls and powers. Fire alarm systems include fire detection and
alarm notification, voice communications, guard's tour, sprinkler waterflow and sprinkler
supervisory systems. NFPA 72, National Fire Alarm Code provides other fire alarm system
requirements.
As you study this material, pay close
attention to the illustrations, which highlight important requirements. Many people have
difficulty understanding Article 760 from the text alone, and the figures also show you
common Article 760 violations.
accessible portions of abandoned fire alarm cables must be removed.
- New FPN alerts the Code user
to a comprehensive standard that identifies what "installed in a neat and workmanlike
manner" means. And revised text specifies that fire alarm raceways and cables
must be secured in place and the ceiling support wires or ceiling grid cannot be used
for this purpose.
- New rule prohibits AFCI protection
of the 120V circuit that supplies power for a nonpower-limited fire alarm system.
of the 120V circuit that supplies power for a power-limited fire alarm system.
clarify that "power-limited equipment" supplying power-limited fire alarm
circuits must be durably marked to indicate each power-limited circuit. This change
was necessary because some wiring method manufacturers have advertised boxes and raceways
identified only with the "color red" as meeting this requirement.
- Additional text clarifies when
nonpower-limited wiring and power-limited cables can be installed together in the
same conduit. For example, pull stations or smoke detectors could be wired with Type
FPL cable and the horns or strobes could be wired with THHN conductors.
of audio system circuits in the same cable or raceway as power-limited fire alarm
conductors or cables.
ARTICLE 770 Optical Fiber Cables
and Raceways
Article 770 provides the requirements
for installing optical fiber cables and special raceways for optical fiber cables. It
also contains the requirements for composite cables, often-called "hybrid,"
that combines optical fibers with metallic current-carrying conductors.
While we normally think of Article 300
when we think of wiring methods, you need to use only Article 770 methods for fiber-optic
cables, except where Article 770 makes specific references to Article 300. The first such
reference, in 770.3, is to 300.21. This addresses requirements for stopping the spread
of combustion. Another Chapter 3 reference is to 300.22, which applies if you're installing
optical fiber cables and optical fiber raceways in ducts, plenums, or other air-handling
spaces.
Article 770 doesn't refer to 300.15,
so you do not have to use boxes for splices or termination of optical fiber cable. The
FPN in 770.113 states that splice cases and terminal boxes are typically used as enclosures
for splicing or terminating and splicing optical fiber cables. While this is a good practice,
it's not required-no FPN is an enforceable Code requirement [90.5(C)].
Article 90 states that the NEC isn't
a design guide or installation manual. Article 770 doesn't tell you how to ensure your
system will meet, and test out to, the performance requirements you need or your contract
specifies. For example, it doesn't mention bend radii. It doesn't tell you how to install
and test cable safely, either, but that doesn't mean you should look into a cable, even
if you cannot see any light coming through it. Light used in fiber-optic circuits usually
isn't visible, but it can damage your eye.
the accessible portion of abandoned optical fiber cables must be removed.
- New subsection permits listed
optical fiber raceways to be installed as innerduct in any Chapter 3 raceway.
manner" means. And revised text specifies that optical fiber raceways and cables
must be secured in place and that ceiling support wires or the ceiling grid are not
permitted for this purpose in accordance with 300.11
- Because unlisted optical fiber
entrance cables can contribute to a fire and smoke hazard, the exception was revised
to prohibit the installation of unlisted optical fiber entrance cables in risers,
ducts, plenums, and other space used for environmental air.
Mike Holt's
Comment: If you desire more information about any of the above changes, be
sure to order my Changes
book and/or library (Video/DVD).
12a.
NEC Code Changes Textbook |
Mike
Holts Illustrated Changes to the NEC 2005 textbook is here!
So, get ready now!
The 2005 NEC
is here and its time to adapt. Dont let the scale of this
change intimidate you. With Mike Holts Illustrated Changes
to the NEC 2005, youll be up-to-speed in no time. Nearly
5,000 changes were proposed for the 2005 NEC! Over 225 of them
will have a significant impact on designing, installing and inspecting
electrical systems. Mike takes you through these changes, which
he considers to be of critical importance. Youll be able
to easily gauge how these changes will impact your work and apply
them instantly. This 120-page comprehensive full-color textbook
includes 198 color illustrations for reference. Subjects include:
General Requirements, Circuits and Protection, Grounding versus
Bonding, Wiring Methods, Equipment for General Use, Special Occupancies,
Special Equipment, Special Conditions, and Limited Energy and
Communications Systems.
Why does Mikes
book give you an edge? Because of the extra effort put forth to
organize these changes in an easy-to-follow manner. Each change
includes:
- Cross references
to other related Code requirements to help you develop a better
understanding of how the Code rules relate to one another.
- Background
information for each change along with explanations, which
are delivered in Mikes trademark style
easy-to-understand.
- Authors
These sections were written by Mike to help you better
understand the NEC material, and to bring to your attention
things he believes you should be aware of.
- Full-color
detailed graphics to reinforce those difficult concepts and
provide instant understanding.
Product Code:
05BK
ISBN: 1-932685-27-8
Pages: 120
Illustrations: 198