NM-B Cable vs. Types of Constructions

By Mario Valdes,
Mike Holt Enterprises

INTRODUCTION
The purpose of this article is to provide the electrician with familiarity of the installation of non-metallic sheathed cable (Type NM) and construction type restrictions.

The building code limits construction types based on occupancy classification, building height and allowable area. Type NM cable consist of a PVC jacket that’s moisture resistant and flame-retardant, paper sheathing separator with 90°C rated conductors.

Why non-metallic sheath cable is not allowed in certain structures is a controversial topic; in simple terms you cannot have a combustible wiring method (Type NM cable) in non-combustible construction.

Let’s examine the construction types to further clarify uses permitted and uses not permitted for Type NM cable.

TYPE I: FIRE RESISTIVE CONSTRUCTION
Non-metallic sheathed cable is not permitted in a Type I construction building [334.12(A)(1)].

In Type I construction, the structural elements consist of non-combustible material. The exterior is usually concrete and the interior partitions typically consist of metal framing.
The buildings are allowed of unlimited heights if sprinkled in accordance with the building code.

  • Examples of Type 1 construction include high rise buildings, parking garages, stadiums, and arenas.
 
 

TYPE II: NON COMBUSTIBULE CONSTRUCTION
Non-metallic sheathed cable is not permitted in a Type II construction building [334.12(A)(1)].

In Type II construction, the structural elements consist of non-combustible material with a lesser fire rating than Type 1 construction. The exterior is usually bolted or welded steel and the interior partitions typically consist of metal framing. The buildings have different height limitations depending on if sprinkled or non-sprinkled in accordance with the building code. Examples of Type II construction include big box supermarkets, strip malls, warehouses, and school.

  • Examples of Type II construction include big box supermarkets, strip malls, warehouses, and schools.
 
 

TYPE III: ORDINARY CONSTRUCTION
Non-metallic sheathed cable is permitted in Type III construction buildings for one or two family dwellings, multifamily dwellings and other structures where concealed within a 15 min finish rating (1/2’’ drywall) [334.10(1),(2),(3)].
In Type III construction, the structural elements consist of non-combustible material for the exterior, usually concrete or block wall. The interior partitions are made of combustible materials, typically wood framing. Type III construction buildings are allowed up to 6 stories if sprinkled in accordance with the building code.

  • Examples of Type III construction include houses, duplexes, apartment buildings and mid-rise condominiums, and commercial buildings.

 
 

TYPE IV: HEAVY TIMBER CONSTRUCTION
Non-metallic sheathed cable is permitted in Type IV construction buildings for one or two family dwellings, multifamily dwellings, and other structures where concealed within a 15 min finish rating (1/2’’ drywall) [334.10(1),(2),(3)].

In Type IV construction, the structural elements consist of consists of heavy timber. The exterior is non-combustible fire treaded heavy timber and the interior partitions are combustible heavy timber framing. Type IV construction buildings are allowed up to 6 stories if sprinkled in accordance with the building code.

  • Examples of Type IV construction include old factory mills, worship churches and wood cabins.
 
 

TYPE V: COMBUSTIBULE CONTRUCTION
Non-metallic sheathed cable is permitted in Type V construction buildings for one or two family dwellings [334.10(1),(2),(3)].

In Type V construction the structural elements consist of combustible material. The exterior is usually wood panels and the interior partitions are typically wood framing.
Type V construction buildings are allowed up to 5 stories if sprinkled in accordance with the building code.

• Examples of Type V construction include single family homes and townhouses.

 
 

SUMMARY
Understanding construction types can really make a difference as it relates to the usage of Type NM cable, there is no doubt Type NM cable is the most cost-effective wiring method and could provide a huge difference in job cost.

If ever in a type I or II construction type building take a look at NEC 334.10(5) as it states NM-B cable is permitted where installed within raceways. As an electrician its really simple, the construction type is shown on approved plans building code compliance analysis located in the front sheet.

Comments
  • Editorial comments: It is fire treated, not fire treaded for heavy timber construction. Also, buildings are sprinklered, not sprinkled. Other than a few other obvious language errors, a good factual article.

    Earl Dean  February 26 2021, 10:27 am EST
    Reply to this comment
  • Reply from: Mario Valdes   February 26 2021, 9:29 pm EST
    Appreciate your feedback.
    Reply to Mario Valdes


  • Great article. It always amazed me how misinterpreted this section was even going back to the 1999 NEC when I feel the first attempt to clarify NM cable was not limited to residential and multi-family construction. 1999 NEC Article 336-5.Uses Not Permitted.(a)(1) In any multifamily dwelling or OTHER STRUCTURE exceeding three floors above grade.

    We would argue within our own Building Department what the meaning of "other structure" was implying. The point I got out of this article and always push in the field is to look at the Code Analysis on the front of the APPROVED PLANS to determine the appropriate wiring method. A single story multifamily of Type-II construction would prohibit NM cable but the same building of Type-V would allow it. But if this same Type-V building has the drawings stamped and signed by an Electrical Engineer of Record and they state EMT shall be used, then you will be stuck with that until you can hopefully talk them into a plan change. The only point of clarification I would make to this article is that Type-V construction is not limited to single and multifamily dwelling units. There are other occupancies like (B) Office, (M) Mercantile and (S) Storage occupancies that if designed properly could be of Type-V construction and would allow the use of NM cable as an approved wiring method. In the end there will always be strong feelings about what one might believe to be the proper wiring method for a commercial application.

    Mike Adams  February 26 2021, 2:31 am EST
    Reply to this comment
  • Reply from: Mario Valdes   February 26 2021, 9:24 pm EST
    Glad you enjoyed the article and yes you are correct about your Type V construction statement.
    Reply to Mario Valdes


  • To All Can you install SER in a house feeding from a generator outside to the ATS in the basement of a house? From the utility meter to the ATS SEU and from the ATS to the panel SER?

    william schumacher  February 26 2021, 2:31 am EST
    Reply to this comment
  • Reply from: Mike Holt   February 26 2021, 11:53 pm EST
    Please post your question on MikeHolt.com/Forum
    Reply to Mike Holt


  • Nice descriptions, pictures and examples but why is NM not allowed in certain structures.

    Dave  February 26 2021, 1:30 am EST
    Reply to this comment
  • Reply from: Mario Valdes   February 26 2021, 9:28 pm EST
    The 'why' is a controversial topic. In simple terms you cannot have a combustible wiring method in non-combustible construction.
    Reply to Mario Valdes


  • This article reminded me of something we went through 4 years ago here in Eugene OR as regards Type NM-B cable. One of the draw backs to using type NM-B cable in a Type V combustible building (specifically a 5 story multi-family building) is that most inspectors and municipality will not allow you to install it until the building is "dried in". Meaning, topped out, weather tight roof and exterior walls. However, by enlisting the member of the Underwriters Laboratories who actually wrote the UL listing for Type NM-B along with the manufacturer's rep from Southwire who oversees their Type NM-B construction, a representative from the NEC, a former member of the state of Oregon electrical board and a few others we were able to convince the director of the building department for the city of Eugene that the UL listing for Type NM-B cable as UL listed for use in an NEC defined area as "normally dry" does not preclude neither should it preclude the ability to install the cables as the building is going up whether there's a roof on it or not. We had ONE inspector who was all against it but that turned out to be a grudge he held against the GC on the job and he didn't get his way. The city allowed it on one building we were building at the time with one caveat... they wanted us to have 2 floors of flooring down above us before we began roughing in the cable. Even with this caveat it saved a lot of time on the schedule. Otherwise we would have had to wait until the building was topped out and ALL the other trades in our way before we could begin. Unfortunately the problem inspector convinced the dept director to rescind the allowance after the project was completed because, he complained, we took advantage of their allowance by ALSO installing boxes which had steel nails which might rust in weather. Cheap shot but that time he got his way. Because of the trend to build a lot of 5 story above podium wood multi-family buildings this is going to become more and more vital to schedules and I'd love to see others jump on this bandwagon to push the municipalities across the country and AHJ's to allow romex to be installed without dry cover in place since it meets the code intention of a normally dry place (look up the definition in Art 100). Southwire was on board with this as was the UL guy. I think many would welcome this change.

    S Leuck  February 26 2021, 12:34 am EST
    Reply to this comment


Get notified when new comments are posted here
* Your Email:
 
        
 
Add Your Comments to this Newsletter
* Your Name:
   Your name will appear under your comments.

* Your Email:
   Your email address is not displayed.
* Comments:

Email Notification Options:
Notify me when a reply is posted to this comment
Notify me whenever a comment is posted to this newsletter