Do you know the specific locations where GFCI and AFCI protection are required?

A ground fault interrupter (GFCI) protects people from shock, while an arc fault interrupter (AFCI) protects people from fires that could result from electrical arcing of wiring inside walls. Following the NEC rules will optimize protection, while noncompliance could prove fatal to occupants.

GFCI protection for dwellings
GFCI protection must be provided as required in 210.8(A) through (F). GFCI protective devices must be in a readily accessible location.

You can provide the GFCI protection using either a GFCI circuit breaker or a GFCI receptacle. To apply 210.8(A)(8) or (10), 210.8(B)(7), (13), and (15), the distance you measure from the sink or bathtub/shower is the shortest path the power-supply cord connected to the receptacle will follow without piercing a floor, wall, ceiling, or fixed barrier.

With the 2023 revision, the reference to windows and doors was removed to ensure GFCI protection for receptacles within the measured distance as required in 210.8 even if the measurement line passes through a window or door.

A GFCI circuit breaker provides ground-fault protection starting at the breaker, so the entire circuit has ground-fault protection. A GFCI receptacle provides ground-fault protection for whatever is plugged into it; it has load-side terminals that provide downstream protection for any other receptacle(s) or device(s) on the circuit.

Receptacles installed in the following dwelling unit locations must be GFCI protected (and the GFCI device must be in a readily accessible location) [210.24(A)]. Figure 01
(1) Bathrooms.
(2) Garages and accessory buildings.
(3) Outdoors.
(4) Crawl spaces (at or below grade).
(5) Basements.
(6) Kitchens.
Traditionally this requirement applied only to kitchen countertop receptacles, but now any cord-and-plug-connected appliance in the kitchen such as the range receptacle, refrigerator receptacle, disposal receptacle, and microwave receptacle now require GFCI protection.
(7) Food or beverage preparation or cooking areas.
(8) Sinks (receptacles within 6 ft of the top inside edge of the bowl of a dwelling unit sink).
(9) Boathouses.
The Code does not require installing a receptacle in a boathouse, but any that are in a boathouse must be GFCI protected.
(10) Bathtubs or shower stalls (receptacles within 6 ft of the outside edge of a bathtub or shower stall not installed within a bathroom).
(11) Laundry areas.
(12) Damp and Wet Locations Indoors.

Ex 1: GFCI protection is not required for a receptacle dedicated to fixed electric snow-melting equipment if the receptacle is not readily accessible and ground-fault protection of equipment (GFPE) is provided as required by 426.28 and 427.22.

Ex 2: GFCI protection is not required for a receptacle supplying only a permanently installed premises security system.

Ex 4: GFCI protection is not required for receptacles in dwelling unit bathroom exhaust fans, unless specified by the fan instructions.

The receptacle for exhaust fans is internal to the exhaust fan. They are not accessible as a convenience cord-and-plug receptacle, therefore GFCI protection is not required. Per UL Guide Information GPWX, exhaust fans installed in the area directly above the footprint (width and depth of the equipment) of the bathtub or shower must be GFCI protected.

GFCI protection for other than dwellings
GFCI protection is required for 125V through 250V receptacles supplied by single-phase branch circuits 50A (or less) or three-phase branch circuits 100A (or less) installed in the following locations [210.8(B)]:
(1) Bathrooms.
(2) Kitchens.
(3) Food or beverage preparation or cooking areas.
(4) Buffet serving areas (if they have permanent provisions for food serving, beverage serving, or cooking).
This requires GFCI protection for receptacles in the break area of a commercial occupancy.
(5) Rooftops.
(6) Outdoors.
(7) Sinks (for cord-and-plug-connected fixed or stationary appliances within 6 ft from the top inside edge of the bowl of a sink).
Note that a faulted appliance in proximity to sinks presents a shock hazard whether the receptacle is within 6 feet or not.
(8) Indoor damp or wet locations.
(9) Locker rooms.
(10) Garages, accessory buildings, and similar areas.
(11) Crawl spaces (at or below grade).
(12) Unfinished areas of basements.
(13) Aquatic tanks or bowls (receptacles within 6 ft from the top inside edge or rim, and receptacles within 6 ft from the conductive support framing of the container for aquariums, bait wells, and similar open aquatic containers such as tanks or bowls).
(14) Laundry areas.
(15) Bathtubs and shower stalls (receptacles within 6 ft of the outside edge of a bathtub or shower stall not installed in a bathroom).

Ex 2: Rooftop GFCI receptacles are required to be readily accessible only from the rooftop itself.

GFCI protection is also required for:

  • 20V lighting outlets in crawl spaces [210.8(C)]. A lighting outlet is not required for a dwelling unit crawl space unless the space is used for storage or has equipment requiring servicing [210.70(C)].
  • Appliances rated 150V or less to ground, rated 60A or less, single- or three-phase, either cord-and-plug or hardwired connected. A dozen of these are listed in [210.8(D)]. They include vending machines, sump pumps, and electric ranges. Some appliances listed in 210.8(D) may be hardwired instead of cord-and-plug connected, but the GFCI protection requirements of 210.8(A) and (B) apply only to receptacles. So why are these also required to be GFCI protected? Because the shock hazards exist whether appliances are hardwired or cord-and-plug connected. Provide GFCI protection for the appliance branch circuit or outlet, either way.
  • Equipment requiring servicing [210.8(E)]. This includes the 125V, 15A or 20A service receptacle outlet installed within 25 ft of the air-conditioning equipment as required in 210.63(A) or indoor service equipment as required in 210.63(B).
  • All outdoor outlets rated 50A or less located outside a dwelling and outside garages, accessory buildings, or boathouses of dwelling spaces.

If equipment connected to any of the above outdoor outlets is replaced, the circuit to the outlet must be GFCI protected.

Ex 2: GFCI protection is not required for listed HVAC equipment, such as motor compressors or heat pumps.

AFCIs
An AFCI is intended to de-energize the circuit when it detects the current waveform characteristics unique to an arcing fault [100].

AFCI protection is required per 210.12(B) through (C) and the AFCI device must be in a readily accessible location. AFCI protection is not required for outlets in bathroom areas, garages, or outside. But it is required for 15A or 20A, 120V branch circuits in the following dwelling unit locations [210.12(B)]:
(1) Kitchens
(2) Family rooms
(3) Dining rooms
(4) Living rooms
(5) Parlors
(6) Libraries
(7) Dens
(8) Bedrooms
(9) Sunrooms
(10) Recreation rooms
(11) Closets
(12) Hallways
(13) Laundry areas
(14) Similar areas

AFCI protection is required for 15A or 20A, 120V branch circuits in the following dormitory unit locations [210.12(C)]:
(1) Bedrooms
(2) Living rooms
(3) Hallways
(4) Closets
(5) Bathrooms
(6) Similar rooms

AFCI protection is required for 15A and 20A, 120V branch circuits in the following other occupancy locations 210.12(D)]:
(1) Guest rooms and guest suites of hotels and motels.
(2) Nursing homes and limited care facilities, areas used exclusively as patient sleeping rooms.
(3) Areas designed for use exclusively as sleeping quarters in fire stations, police stations, ambulance stations, rescue stations, ranger stations, and similar locations.

If 15A or 20A, 120V branch-circuit wiring is extended, modified, or replaced in any of the areas specified in 210.12(B), (C), or (D), the wiring must be AFCI protected by one of the following [210.12(E)]:
(1) AFCI circuit breaker.
(2) AFCI receptacle installed at the first receptacle outlet of the existing branch circuit.

Ex: AFCI protection is not required for extension wiring that is less than 6 ft long if no outlets or devices, other than splicing devices, are added. This measurement does not include the conductors inside an enclosure, cabinet, or junction box.

Ensuring compliance
When reviewing installation plans, double-check those plans against the why behind the Code requirements.

Ask yourself if a person is likely to interact with the branch circuit by plugging things in. If so, the Code probably requires GFCI protection. With an AFCI, the original question was whether people might not detect arcing in the branch circuit due to being asleep. The concept has expanded somewhat, but unawareness of the hazard is still the main driver.

Learn more with Mike's Understanding the NEC Complete Library:


Comments
  • I am not an electrician, nor sophisticated with home repairs. We need to replace two electrical panels in Oakland California which contain the circuit breakers for most of our house (I believe they contain all the circuit breakers other than for our electric car charger). In order to get a building permit from the City of Oakland, do we need to use AFCI breakers or can we use GFCI breakers which appear to be far less expensive. We are not moving the panels, just replacing them. Thank you.

    Gary Greenfield  April 24 2025, 9:17 pm EDT
    Reply to this comment
  • Reply from: Mike Holt   April 24 2025, 9:31 pm EDT
    Check with the Inspector.
    Reply to Mike Holt


  • Mike Holt, Thank you, you and your team are the best! I have used your books and materials to help me pass all my Journey man, and Master electrical test in 3 states. Does 210.8(B) Applies to washing machines in a laundromat. washing machines with VSD. I did some reading on VSD and found out it's known for causing nuisance tripping.

    Dany Gomes  February 1 2025, 3:43 pm EST
    Reply to this comment
  • Reply from: Mike Holt   February 2 2025, 1:48 pm EST
    Yep...
    Reply to Mike Holt


  • I am replacing AL wiring to my kitchen all the way back to the oanel. I am told I have to use afci/gfci breaker versus a afci/gfci receptacle at the begining of the branch circuit. Can you clarify?

    Neil Ford  January 28 2025, 4:55 pm EST
    Reply to this comment
  • Reply from: Mike Holt   January 28 2025, 11:43 pm EST
    If you are an electrical professional, post your question on MikeHolt.com/Forum.
    Reply to Mike Holt


  • Mike! do Commercial washers need GFCI protection? NEC 210.8 (14)

    Dany  January 26 2025, 1:02 am EST
    Reply to this comment
  • Reply from: Mike Holt   January 26 2025, 2:01 pm EST
    Yes, why do you ask? Is it not clear?
    Reply to Mike Holt


  • What type of breaker should be used for a gas fireplace in a finished basement? The FP has electric ignition and LED accent lighting. I was told by an electrician that an AFCI will trip with a spark ignitor. T or F?

    Steve Fogarty  January 2 2025, 10:33 pm EST
    Reply to this comment
  • Reply from: Mike Holt   January 3 2025, 12:59 am EST
    Please post your question on MikeHolt.com/Forum
    Reply to Mike Holt


  • The picture needs to be corrected. The receptacle in the hallway needs to be GFCI protected because it is within 6’ of the inside edge of the hall bathroom sink. It’s not highlighted as it should be.

    My question is, can it be on the bathroom GFCI circuit for which code states no other outlets. I’ll have to do more reading for I don’t have the code with me at this time

    Richard  December 30 2024, 8:45 pm EST
    Reply to this comment
  • Reply from: Mike Holt   January 1 2025, 1:43 am EST
    I'll move the receptacles so it's not a question. Thanks and Happy New Year
    Reply to Mike Holt

    Reply from: Mike Holt   January 1 2025, 1:49 am EST
    I'll move the two receptacles so that this is not a question. Thanks and Happy New Year.
    Reply to Mike Holt


  • I live in Pittsburgh PA. If I upgrade a service, do I need to install arc fault breakers? I am not adding or extending any circuits. "The NEC doesn't require AFCI's on a panel upgrade as long as the existing circuits aren't extended more than 6'. "

    rick  November 24 2024, 1:44 am EST
    Reply to this comment
  • Reply from: Mike Holt   November 25 2024, 12:18 am EST
    I think not, but check with AHJ. MikeHolt.com/AHJ
    Reply to Mike Holt


  • I am slightly confused. My inspector told me i needed a GFCI Breaker within 25 feet of the new Mini Split i installed. But if i am reading this newsletter correct. It GFCI isn’t required for listed HVAC equipment such as compressors and heat pumps. Can you clarify and give me the cite to show my inspector.

    Cris M  October 24 2024, 2:07 am EDT
    Reply to this comment
  • Reply from: Mike Holt   October 24 2024, 3:07 am EDT
    GFCI protection is not required for the HVAC equipment, see 210.8(F) Exception 2.
    Reply to Mike Holt

    Reply from: Richard Weber   October 25 2024, 12:44 am EDT
    From the language you used, what got my attention is he may be referring to the code requiring a plug within 25ft of any equipment requiring servicing. If the equipment is outside it would need to be gfci protected as well. As said by Mr. Holt there is no requirement to gfci HVAC equipment. An everyday example of that is in-wall Heaters, when installed they are fused with a standard thermal trip breaker, not an AFCI or GFCI
    Reply to Richard Weber

    Reply from: Curt A   November 4 2024, 1:28 am EST
    I believe he is referring to a Gfci protected outlet within 25ft of the unit for servicing it the unit
    Reply to Curt A

    Reply from: Mike Holt   November 4 2024, 4:53 pm EST
    Correct
    Reply to Mike Holt


  • So on a rental inspection they said the SE cable has to be replaced. Now the city wants a 100amp disconnect outside. Does that mean that the arc fault devices (breakers) need to be added or installed in the panel? Or is it for new construction or remolding?

    Rob  October 10 2024, 1:01 am EDT
    Reply to this comment
  • Reply from: Mike Holt   October 10 2024, 4:56 am EDT
    Post your question on MikeHolt.com/Forum
    Reply to Mike Holt


  • I work in a commercial building with kitchen/break rooms on all floors. My question is, are AFCI breakers an exception for GFCI outlets? The outlets are labeled GFCI protected, yet no GFCI in the kitchen area. However, they have AFCI breakers in our riser rooms.

    TR  September 23 2024, 4:23 pm EDT
    Reply to this comment
  • Reply from: Mike Holt   September 24 2024, 9:47 am EDT
    Please post your question on MikeHolt.com/Forum
    Reply to Mike Holt


  • Are AFCi breaker required for electric water heater electric stove and electric dryers in Tennessee Don't find any dual function SD QO AFCI In searches only GFCI with pig tails

    Pops  September 15 2024, 10:23 pm EDT
    Reply to this comment
  • Reply from: Mike Holt   September 16 2024, 1:37 pm EDT
    Please post your question on MikeHolt.com/Forum
    Reply to Mike Holt


  • I have an inspector requiring AFCI protection on a kitchen hood and refrigerator. But I don't see where this is specified in the code? Anyone else encountering this requirement? Having the refer on an afci seems odd since the compressor could trip this very easily. Thank you!

    Michellle  April 18 2024, 3:26 pm EDT
    Reply to this comment
  • Reply from: Mike Holt   April 20 2024, 12:03 pm EDT
    Please read 210.12(B), it requires all circuits to be AFCI protected. In addition, those loads will not trip the AFCI unless there is a problem with the circuit or load.
    Reply to Mike Holt

    Reply from: Sean   August 29 2024, 10:44 pm EDT
    Afci causes Brand new refrigerator to trip a $9,000 german made fridge Trips weekly in Cycle as regular Change breaker Wire from panel to refridge is less then 12 feet and fully visible in The basement to the kitchen Try telling your client that they're $9,000 refrigerator that's brand new is the problem AFC eyes do not work that's why so many companies have switched over to DC Drive systems because afci's cause so many faults afci's are ridiculous they should be gotten rid of and the code adopts them because the code Kow tows to insurance companies and manufacturers of the products the NEC should be torn up and rewritten there has been no higher fire danger without afcis than with them
    Reply to Sean

    Reply from: John   November 25 2024, 2:21 am EST
    I just had a house built, but the AFCI breakers are not working for any of the Frigidare appliances. Not sure who is at fault here, the appliances, electrician or the siemens dual purpose breakers . Totally aggravated!!!
    Reply to John

    Reply from: Mike Holt   November 25 2024, 4:27 pm EST
    I know... it really is a problem.
    Reply to Mike Holt


  • Mike,you sound like a politician. Try living in the real world.

    Joseph Anderson  January 21 2024, 9:35 am EST
    Reply to this comment
  • Reply from: Mike Holt   April 20 2024, 12:05 pm EDT
    I think you are quite confused... this newsletter is describing the NEC requirements of 210.12 AFCIs.' This is not my option, so my newsletter is related to the 'real world.'
    Reply to Mike Holt

    Reply from: Bret   August 19 2024, 9:47 pm EDT
    Mike Holt you Rock! You have been extremely helpful over the many years. Thank you very much for all the help to clarify the NEC.
    Reply to Bret


  • can a GFCI be installed on the same circuit as a arc fault breaker?

    Richard Rodkey  December 27 2023, 5:45 pm EST
    Reply to this comment
  • Reply from: Mike Holt   April 20 2024, 12:06 pm EDT
    Yep, no problem at all.
    Reply to Mike Holt


  • Thank you for this article. So there is some overlap based on current code then? Ex: in a kitchen, countertop receptacles must be GFCI and AFCI? How is the dependability of combination devices? Is the independent testing robust enough? That's a lot of things going on in a tiny jbox.

    Alex K  December 23 2023, 12:01 pm EST
    Reply to this comment
  • Reply from: Mike Holt   December 28 2023, 11:26 am EST
    The technologies are totally different, I'm sure UL has this all worked out, and they have been available for about five years.
    Reply to Mike Holt

    Reply from: Sean T Gallagher   August 29 2024, 10:46 pm EDT
    Anyone telling you afci technology works is and should be laughed at companies that make fans and exhaust fans for bathrooms and ceiling fans and other devices have switched over to DC Drive because the Arc in the motor causes afci to trip constantly refrigerators are now becoming DC Drive systems as well because they trip and cost them thousands of dollars of food losses every day afci technology is bunk and it's bullshit and it causes electricians more pain than it solves and now they want to make us use combination protecting an entire circuit with an afci GFI combination is ridiculous
    Reply to Sean T Gallagher


  • With all the trouble we used to have with these AFCI's makes me glad I retired couple years ago

    Marshall Peterson  December 19 2023, 11:17 am EST
    Reply to this comment

  • I was told that the code requirement 210.8f has been suspended due to nuisance tripping. Can you confirm this or deny?

    Thanks

    Jeffery Van Nocker  December 19 2023, 10:57 am EST
    Reply to this comment
  • Reply from: Mike Holt   December 19 2023, 11:40 am EST
    False, however, there was a TIA for the 2020 NEC to not require GFCI for a/c equipment and the 2023 added an exception to not require GFCI for a/c equipment. See: www.ecmweb.com/national-electrical-code/article/21166916/two-tias-issued-for-the-2020-nec-regarding-gfci-protection
    Reply to Mike Holt

    Reply from: Kurt   March 19 2025, 8:31 pm EDT
    Mike, long time reader first time Wrighter. my question is can I use GFCI instead of AFCI in the AFCI locations?
    Reply to Kurt

    Reply from: Mike Holt   March 19 2025, 9:50 pm EDT
    If the NEC requires GFCI, then AFCI can't be used and if AFCI protection is required, then GFCi can't be used.
    Reply to Mike Holt


  • Is a Horse barn a auxiliary building? I would gfi the tank heaters for the horses regardless but wondering about inside horse arenas/ tackrooms/ barn.

    Devon Van De Kieft  December 18 2023, 7:27 pm EST
    Reply to this comment
  • Reply from: Mike Holt   December 19 2023, 11:31 am EST
    Agricultural buildings (horse barns) have their own GFCI requirements. 547.28 Ground-Fault Circuit-Interrupter Protection. Ground-fault circuit-interrupter (GFCI) protection shall be provided as required in 210.8(B)for areas of agricultural buildings not included in the scope of this article. GFCI protection shall not be required for other than 125-volt, 15- and 20-ampere receptacles installed within the following areas: (1) Areas requiring an equipotential plane

    (2) Outdoors

    (3) Damp or wet locations

    (4) Dirt confinement areas for livestock
    Reply to Mike Holt


  • Mike, what happened to the exception for 30 and 50 amp RV Park hookups?

    Brian  December 18 2023, 7:12 pm EST
    Reply to this comment
  • Reply from: Brian House   February 3 2025, 4:48 pm EST
    GFCI protection is not required for 30A and 50A receptacles in RV Park Equipment. It is not an exception. See 551.71(F)(2)
    Reply to Brian House



Get notified when new comments are posted here
* Your Email:
 
        
 
Add Your Comments to this Newsletter
* Your Name:
   Your name will appear under your comments.

* Your Email:
   Your email address is not displayed.
* Comments:

Email Notification Options:
Notify me when a reply is posted to this comment
Notify me whenever a comment is posted to this newsletter