Grounding of Separately Derived Systems, based on the 2023 NEC
image

Grounding of Separately Derived Systems, based on the 2023 NEC®

By Mike Holt
NEC® Consultant for EC&M Magazine

Note: This article is based on the 2023 NEC.

Do you understand how the grounding and bonding requirements for the separately derived systems?

Figure 01
A “separately derived system” (SDS is an electrical power supply having no direct connection(s) to the circuit conductors of any other electrical source other than those established by grounding and bonding connections [100]. Figure 01

Except for autotransformers, transformers are separately derived because the primary conductors have no direct electrical connection to the secondary conductors.

Transformer SDSs must be bonded and grounded per 250.30(A)(1) through (A)(8). On the load side of the bonding jumper, you cannot connect the neutral conductor to:
  • The transformer case.
  • Metal parts of equipment.
  • Equipment grounding conductors.

System bonding jumper
A “System Bonding Jumper” is the connection between the neutral conductor (or grounded-phase conductor) and the equipment grounding conductor, supply-side bonding jumper, or both at a transformer SDS.

A system bonding jumper must be installed at the secondary neutral point or the secondary disconnect neutral terminal (not both). The system bonding jumper must comply with 250.28 and be sized per 250.102(C).

The grounding electrode conductor must terminate to the point where the system bonding jumper has been installed [250.30(A)(5)].

Ex 2: If a structure is supplied by a feeder from an outdoor transformer SDS, a system bonding jumper at both the source and the first disconnect is permitted if it does not establish a parallel path for the neutral current. The neutral conductor cannot be smaller than the size specified for the system bonding jumper, and it is not required to be larger than the phase conductor(s).

A system bonding jumper at the source connects the secondary neutral point of the system to the metal enclosure of the transformer SDS [250.30(A)(1)(a)]. A system bonding jumper at the first disconnecting means connects the neutral conductor of the transformer secondary to the metal enclosure at the secondary disconnect [250.30(A)(1)(b)].

Supply-Side bonding jumper
A supply-side bonding jumper installed from the transformer enclosure to the secondary disconnect enclosure can be a nonflexible metal raceway or of the wire type.

The supply-side bonding jumper can be RMC, IMC, or EMT run between the transformer SDS enclosure and the secondary system disconnect enclosure. A nonmetallic or flexible raceway must have a supply-side bonding jumper of the wire type.

A supply-side bonding jumper of the wire type must be sized per 250.102(C) based on the size or area of the secondary phase conductors in the raceway or cable.

Example question: What size supply-side bonding jumper is required for flexible metal conduit containing 300 kcmil transformer secondary conductors?
(a) 4 AWG (b) 2 AWG (c) 1/0 AWG (d) 3/0 AWG
Answer: (b) 2 AWG [Table 250.102(C)(1)]

System grounded conductor
The system neutral conductor is not required to be larger than the phase conductors [250.30(A)(3)]. Oversizing the neutral conductor does not solve excessive unbalanced current returning in the neutral. It is merely a coping strategy that still leaves you with the energy waste and other problems related to reliability issues.

Suppose the system bonding jumper is installed at the secondary system disconnect instead of at the transformer SDS, and the neutral is run in a single raceway. In that case, the neutral must be run from the transformer SDS to the secondary system disconnect. It must be sized per Table 250.102(C)(1) based on the size or area of the secondary phase conductor.

What if you run that neutral paralleled in two or more raceways or cables? In that case, you size the neutral conductor(s) in each raceway or cable set connected in parallel based on the largest phase conductor in each raceway or cable using Table 250.102(C)(1). But don’t go smaller than 1/0 AWG.

Grounding electrode conductor
A transformer SDS installed indoors must be grounded to the building grounding electrode system [250.30(A)(4)].

The grounding electrode conductor for a transformer SDS must be sized per 250.66 [250.30(A)(5)]. The grounding electrode conductor must terminate to the neutral conductor at the same point where the system bonding jumper is connected.

To prevent objectionable neutral current from flowing onto metal parts [250.6], the grounding electrode conductor must originate at the same point on the transformer SDS as where the system bonding jumper is connected [250.30(A)(1)].

Ex 1: If the system bonding jumper is a wire or busbar [250.30(A)(1)], the grounding electrode conductor can terminate at the grounding terminal, bar, or bus where the system bonding jumper terminates, instead of on the neutral terminal.

Grounding Electrode Conductor Example 1
Question: What size grounding electrode conductor is required for a 45 kVA, three-phase, 480V to 120/208V transformer when the secondary conductors are sized at 1/0 AWG?
(a) 6 AWG (b) 4 AWG (c) 3 AWG (d) 2 AWG
Answer: (a) 6 AWG [Table 250.66]

Grounding Electrode Conductor Example 2
Question: What size grounding electrode conductor is required for a 75 kVA, three-phase, 480V to 120/208V transformer when the secondary conductors are sized at 4/0 AWG?
(a) 6 AWG (b) 4 AWG (c) 3 AWG (d) 2 AWG
Answer: (d) 2 AWG [Table 250.66]

Grounding Electrode Conductor Example 3
Question: What size grounding electrode conductor is required for a 112.50 kVA, three-phase, 480V to 120/208V transformer when the secondary conductors are sized at 600 kcmil?
(a) 1/0 AWG (b) 2/0 AWG (c) 3/0 AWG (d) 4/0 AWG
Answer: (b) 2/0 AWG

Where there are multiple transformer SDSs, a grounding electrode conductor tap from each of them to a common grounding electrode conductor is permitted [250.30(A)(6)]. This connection must be made at the same point on the transformer SDS secondary as where the system bonding jumper is connected [250.30(A)(1)].

The common grounding electrode conductor can be any of the following [250.30(A)(6)(a)]:
(1) An unspliced conductor at least 3/0 AWG copper or 250 kcmil aluminum.

(2) Interior metal water pipe not more than 5 ft from the point of entrance to the building [250.68(C)(1)].

(3) The metal frame of the building per 250.68(C)(2) or connected to the grounding electrode system by a conductor at least 3/0 AWG copper or 250 kcmil aluminum.

Grounding electrode conductor taps must be sized per Table 250.66, based on the area of the largest secondary phase conductor [250.30(A)(6)(b)].

Ex: If the only electrodes present are ground rods [250.66(A)], concrete-encased electrodes [250.66(B)], or ground rings [250.66(C)], the size of the common grounding electrode conductor is not required to be larger than the largest conductor required by 250.66(A), (B), or (C) for the type of electrode that is present.

Tap connections to the common grounding electrode conductor must be made at an accessible location by any of the following methods [250.30(A)(6)(c)]:
(1) A connector listed as “bonding and grounding equipment.”

(2) Listed connections to aluminum or copper busbars at least ¼ in. thick × 2 in. wide, and of a length to accommodate the terminations necessary for the installation.

(3) Exothermic Welding. Tap grounding electrode conductors must remain without a splice or joint.
If located outdoors, the grounding electrode connection must be made at the transformer SDS [250.30(C).

The grounding electrode conductor must comply with 250.64(A), (B), (C), and (E) [250.30(A)(7)]. For example, the grounding electrode conductor must be copper where within 18 in. of the surface of the Earth [250.64(A)], securely fastened to the surface on which it is carried [250.64(B)(1)], and adequately protected if exposed to physical damage [250.64(B)(2) and (3)]. Also, ferrous metal enclosures enclosing a grounding electrode conductor must be made electrically continuous from the point of attachment to cabinets or equipment to the grounding electrode [250.64(E)].

Ensuring success with SDS
While a source might be separately derived, the rules for grounding and bonding it are not derived from some separate set of physics. Keep two principles in mind when bonding and grounding any SDS.

First, we ground at the source but not on the load side. That is why there’s a grounding connection at an SDS. Second, we bond so there is no difference in potential between non current-carrying metallic objects.