Note: This article is based on the 2026 NEC®.

Do you know what a feeder is, where it starts and ends, and how to size the conductors and overcurrent protection? What about surge protection and barriers?

Introduction
In accordance with Article 100, "Feeders" are the conductors between a service disconnect, transformer secondary, generator output, or other power production sources such as a solar photovoltaic system disconnect and an energy storage system disconnect, and the final branch-circuit overcurrent protective device.

The requirements of feeders within Article 215 are different than those for Services contained in Article 230, and Branch Circuits in Article 210. Therefore, it is important to properly understand the differences between a feeder from a service or branch circuit.

Article 215 contains the general requirements for the installation, conductor sizing, and overcurrent protection, and surge protection for feeder circuits [215.1].

Conductor Sizing
The ampacity of the feeder conductors must be no less than 125 percent of the continuous loads, plus 100 percent of the noncontinuous loads.

Example 1: Continuous and Noncontinuous Loads
Question: What size copper feeder conductors are required for a 100A continuous load and 100A noncontinuous load?
(a) 1/0 AWG (b) 2/0 AWG (c) 3/0 AWG (d) 4/0 AWG
Figure 01

Figure 01

Solution:
Step 1: Determine the minimum conductor ampacity.
Minimum Conductor Ampacity = (100A × 125%) + 100A
Minimum Conductor Ampacity = 125A + 100A
Minimum Conductor Ampacity = 225A
Step 2: Determine the conductor size.
4/0 AWG rated 230A, 75°C column of Table 310.16
Answer: (d) 4/0 AWG

Example 2: Continuous Load Only
Question: What size copper feeder conductors are required for a 180A continuous load?
(a) 1/0 AWG    (b) 2/0 AWG    (c) 3/0 AWG    (d) 4/0 AWG
Solution:
Step 1: Determine the minimum conductor ampacity.
Minimum Conductor Ampacity = 180A × 125%
Minimum Conductor Ampacity = 225A
Step 2: Determine the conductor size.
4/0 AWG rated 230A, 75°C column of Table 310.16
Answer: (d) 4/0 AWG

Overcurrent Protection Sizing
Feeder overcurrent protective devices must have an ampere rating no less than 125 percent of the continuous loads, plus 100 percent of the noncontinuous loads [215.5].

Example: Continuous and Noncontinuous Loads
Question: What size feeder overcurrent protective device is required for a 100A continuous load and a 100A noncontinuous load?
(a) 200A    (b) 225A    (c) 250A    (d) 300A
Solution:
OCPD = (100A continuous load × 125 percent) + 100A noncontinuous load
OCPD = (100A × 125%) + 100A
OCPD = 125A + 100A
OCPD = 225A [240.6(A)]
Answer: (b) 225A

Conductor Identification
The feeder neutral conductor must be identified white or gray in accordance with 200.7 [215.12(A)], and the feeder equipment grounding conductor must be identified green, green with yellow stripe, or bare in accordance with 250.119 [215.12(B)].

Identification of the feeder phase conductors must be as follows:

(1) Feeder phase conductors for premises wiring system with only one nominal voltage system must be identified with other than white, gray, or green in accordance with 310.6(A)(3).

(2) Where the premises wiring system has feeders supplied from more than one nominal voltage system, the feeder phase conductors must be identified by phase and nominal voltage system at termination, connection, and splice points as follows:

(a) Feeder phase conductor identification can be by color coding, marking tape, tagging, or other means approved by the authority having jurisdiction (AHJ).

(b) Feeder phase conductor identification must be readily available or posted at the panelboard.

Identification Sidebar
When a premises has more than one nominal voltage system, the phase conductors must be identified by phase and voltage system. This can be done by permanently posting an identification legend that describes the method used (such as color-coded marking tape or color-coded insulation).

Whichever color scheme is used, it is important that it remains consistent wherever phase conductors are terminated throughout the premises.

The NEC does not require a specific color code for phase conductors, but electricians often use the following colors:

  • 120/240V, single-phase—black, red, and white
  • 208Y/120V, three-phase—black, red, blue, and white
  • 240V/120V, three-phase (high-leg)—black, orange, blue, and white
  • 480Y/277V, three-phase—brown, orange, yellow, and gray; or brown, purple, yellow, and gray. Figure 02

Figure 02

Barriers
During maintenance and servicing, an electrician can be exposed to energized parts on the line side of a feeder tap or transformer secondary conductor termination into an overcurrent protective device; even if the disconnect is in the open position.

Barriers must be placed on energized phase terminals of panelboards or switchboards supplied by the following [215.15]:

  • A feeder tap conductor, see 240.21(B).
  • Transformer secondary conductors, see 240.21(C).

Surge Protection
If a feeder supplies any of the following areas, a Type 1 or Type 2 SPD is required [215.18(A)]:
(1) Dwelling units.
(2) Dormitories.
(3) Guest rooms and guest suites of hotels, motels, and dormitories.
(4) Areas of nursing homes and limited care facilities used exclusively as patient sleeping rooms.
(5) Areas for sleeping quarters in fire stations, police stations, rescue stations, ambulance stations, ranger stations, and similar locations.

The SPD must be installed in or adjacent to the feeder distribution equipment containing the branch circuit overcurrent protective devices [215.18(B)]. Figure 03

Figure 03

Surge protection from surges generated from lightning, electric utility, or utilization equipment is most effective when located closest to the branch circuits [215.18(B) Note].

Surge protection helps protect life-safety electronic equipment like AFCIs, GFCIs, and smoke alarms.

Where feeder-supplied distribution equipment is replaced in dwelling units, dormitories, guest rooms and guest suites of hotels or motels, and areas of nursing homes and limited care facilities used exclusively as patient sleeping rooms, an SPD is required [215.18(D)].

SPDs must have a nominal discharge current rating (In) at least 10 kA [215.18(E)].

Getting Feeders Right

  • Identify the continuous and noncontinuous loads, calculate the feeder load, and properly size the conductors and overcurrent protection.
  • Make sure the feeder conductors are consistently identified throughout the premises.
  • Place barriers on energized phase terminals of panelboards or switchboards in accordance with 215.15.
  • If a feeder supplies any areas listed in 215.18(A)(1) through (5) make sure to install the required SPD.
Learn more with Mike's Understanding The NEC Complete Video Program: