| Significant
Proposals for 2005 NEC Part VI |
As Reviewed by
Mike Holt
The following text
is a quick summary of the proposed changes for the 2005 NEC. This document is
a work in progress and many will be changed by the Code panel over the next few
months. Some of these you might find important to your work and you might want
to follow their progress with me. Therefore, each week I will email you a few
of these changes.
Each proposed change
has a Report on Proposal (ROP) number, like 1-25. This number reflects the Proposal
Number and all action on this proposal can be viewed in the following PDF
document NEC Part2.
As always, I am
looking to improve our products, so if you feel you have anything to contribute,
please let me know at Mike@MikeHolt.com.
V. Bonding
5-185
250.92 Services.
(B) Method of Bonding at the Service. Text revised to require "other approved
devices" used for bonding of service raceways to be "listed."
5-189
250.100 Bonding in Hazardous (Classified) Locations
Change prohibits the use of the grounded (neutral) conductor for bonding metal
parts in hazardous locations. In addition, it clarifies that metal raceways must
be bonded in accordance with this section, whether or not equipment grounding
(bonding) conductors are installed in the metal raceway.
Author's Comment:
The equipment grounding (bonding) conductor inside a metal raceway is not to be
used as a substitute for the bonding requirements of this section.
5-197
250.104 Equipment Bonding Jumpers.
(B) Other Metal Piping. Text revised to clarify when metal piping systems, including
gas piping, is required to be bonded.
5-200
Text revised to clarify the bonding requirements for exposed interconnected structural
steel forms a metal building frame is not intentionally grounded.
5-202
250.112 Fastened in Place or Connected by Permanent Wiring Methods (Fixed) - Specific
Change clarifies that metal parts of electrical equipment must be bonded to the
power supply, not grounded to the earth!
5-216
250.118 Types of Equipment Grounding Conductors.
(5) Flexible Metal Conduit (FMC). New text specifies when an equipment (bonding)
conductor is required to be installed.
5-218
(6) Liquidtight Flexible Metal Conduit (LFMC). New text specifies when an equipment
(bonding) conductor is required to be installed.
5-211
New exception requires a "wire type" equipment grounding (bonding) conductor
in all metal raceways located on rooftops.
Author's Comment:
Strange that an exception contains a requirement that is more stringent than the
general rule.
5- 220
250.119 Identification of Equipment Grounding (Bonding) Conductors
New sentence limits the use of the color green as well as green with yellow striped
insulation to identify equipment grounding (bonding) conductors.
5-219
(A) Conductors Larger Than 6 AWG
(1) Conductor. New exception identifies that equipment grounding (bonding) conductors
4 AWG and larger in conduit bodies are not required to be marked green or green
with a yellow stripe.
5-229
250.122 Size of Equipment Grounding Conductors.
(D) Motor Circuits. Revised text clarifies how to size the equipment grounding
(bonding) conductor for motor circuits.
5-229
(G) Feeder Taps. New rule specifies how to size the equipment grounding (bonding)
conductor for feeder taps.
5-235
250.140 Frames of Ranges and Clothes Dryers.
Section was rewritten to make it easier to understand and apply the bonding requirements
for ranges and clothes dryers.
5-237
250.142 Use of Grounded Circuit Conductor for Grounding Equipment.
(B) Load-Side Equipment. The exception, which permitted the dangerous practice
of bonding the meter enclosures to the grounded (neutral) on the load side of
the service disconnect, was deleted.
Author's Comment:
Meter enclosures are now readily available with neutral terminations that can
be insulated from the metal enclosure.
5-239
250.146 Connecting Receptacle Grounding Terminal to Box.
(A) Surface Mounted Box. New sentence clarifies how to ensure direct metal-to-metal
contact between the metal mounting yoke of a receptacle and the metal box, when
a bonding jumper is not installed from the grounding (bonding) terminal of the
receptacle.
Author's Comment:
This rule only applies when relying on direct contact from the device yoke to
a metal box for bonding.
5-238a
(B) Contact Devices or Yokes. This section for "self-grounding receptacles"
was revised to require the receptacle to be "listed as self-grounding".
5-244a
250.147 Bonding of General-Use Snap Switches
The bonding requirements for general use snap switches were relocated from 404.9(B)
to this section.
5-248
250.148 Continuity and Attachment of Equipment Grounding Conductors to Boxes.
Changes include formatting into subsections with titles and editorial improvements.
Article 280 Surge Arresters
5-262
280.4 Surge Arrester Selection.
(A) Circuits of Less Than 1000 Volts.
(3) Short-Circuit Rating. New item clarifies when surge arresters are required
to be marked with a short circuit current rating and where they cannot be installed
because of excessive fault current.
Article 285 Transient Voltage Surge Suppressors: TVSSs
5-267
285.3 Uses Not Permitted.
Text revised in item (2) on when transient voltage surge suppressors are permitted
on ungrounded systems, impedance grounded systems, and corner grounded delta systems.
Chapter 3 Wiring Methods and Materials
Article 300
Wiring Methods
3-24
300.4 Protection Against Physical Damage
(A) Cables and Raceways Through Wood Members.
(1) Bored Holes. New exception permits nail plate less than 1/16 in. thick if
listed for this purpose and marked so the inspector can verify its listing.
Author's Comment:
Hardened steel plates thinner than 1/16 inch have been tested and found to provide
better protection from screw and nail penetration than the thicker plates.
3-26
(2) Notches in Wood. Additional requirement permits nail plate less than 1/16
in. thick if listed for this purpose and marked so the inspector can verify its
listing.
3-27
(2) Notches in Wood. New exception permits nail plate less than 1/16 in. thick
if listed for this purpose and marked so the inspector can verify its listing.
3-28
(B) Nonmetallic-Sheathed Cables and Electrical Nonmetallic Tubing Through Metal
Framing Members.
(2) Nonmetallic-Sheathed Cable and Electrical Nonmetallic Tubing. New exception
permits nail plate less than 1/16 in. thick if listed for this purpose and marked
3-17
(D) Cables and Raceways Parallel to Framing Members and Furring Strips. Text revised
to expand the requirements when the 1-1/4" cable clearance is required when
the cable is run parallel to framing members.
3-33
(D) Cables and Raceways Parallel to Framing Members and Furring Strips. New exception
3-33
(E) Cables and Raceways Installed in Shallow Grooves.
New exception permits nail plate less than 1/16 in. thick if listed for this purpose
3-51
300.6 Protection Against Corrosion and Deterioration.
This section was re-written to better cover all possible types of corrosion or
deterioration to metallic systems. In addition, the text was revised to make it
clear that where corrosion-resistant compound is required to be listed.